GPIO Fire Mute AHM-64

Forums Forums Other A&H products GPIO Fire Mute AHM-64

This topic contains 7 replies, has 3 voices, and was last updated by Profile photo of switchwire switchwire 6 months, 1 week ago.

Viewing 8 posts - 1 through 8 (of 8 total)
  • Author
    Posts
  • #115981
    Profile photo of switchwire
    switchwire
    Participant

    Hi-
    How does one setup a fire mute using the GPIO input on the AHM-64 ?
    Can’t seem to find any documentation or instructional video. Hoping to not need any additional hardware/card.
    Need to setup a contact for the Alarm/Fire panel to trip.

    #115984
    Profile photo of KeithJ A&H
    KeithJ A&H
    Moderator

    @switchwire

    In AHM system manager, navigate to Configure/Controllers and then select in the Unit list, select Unit GPIO.
    You can then select GPI 1 or GPI 2 and using the drop down, choose for it to trigger an Input, Zone, Control Group, or Crosspoint Mute.
    Then you just need to select the channel and how the mute will work.

    Hope this helps, but if you’re still having trouble, you can contact us directly through support.allen-heath.com

    Thanks,
    Keith.

    #116045
    Profile photo of switchwire
    switchwire
    Participant

    Thanks Keith!
    I see that area in the software, thanks.
    On the wiring block I see the GPIO “In” and there is a “1”, a “2” and a “down arrow”. What would be the wiring for an alarm/fire panel wire pair? One wire to the “1” and one wire to the “down arrow” ?
    Thanks

    Attachments:
    You must be logged in to view attached files.
    #116051
    Profile photo of Brian
    Brian
    Participant

    It really depends on how your alarm system is configured. The AHM is set up to work in a lot of different scenarios. Is the contact on the alarm system “normally open” (NO) or “normally closed” (NC), etc, etc, etc?

    #116054
    Profile photo of switchwire
    switchwire
    Participant

    Hey Brian,
    The alarm can do either NO or NC. I am trying to test with a bare wire and can’t seem to get the Mute to trip… I have setup “press” to be “closed” and “released” to be “open” between a wire to the GP input “1” and “ground” pins.

    Of course , they have a fire inspection tomorrow and I am onsite just pulled in today to get this setup… 🙂

    #116055
    Profile photo of switchwire
    switchwire
    Participant

    In other words, the little GUI for GP1/GPI corresponds to what on the terminal block on the back?

    #116060
    Profile photo of Brian
    Brian
    Participant

    On the back, there are just three pins for inputs (signals going into the AHM device). GP1 and GP2 obviously relate to the applicable GPIO input. The other pin is a common ground. Depending on the alarm system, you might be able to directly connect the two systems (Alarm GPIO out to AMH GPIO in), but other times you might need a power supply added to the system as well. I’ll post this as a generic example of some of the ways GPIO systems are wired. I have no idea how you will need to wire your system, although you should start by checking the alarm installation manual for their recommendations on using the GPIO outputs.

    https://support.biamp.com/Vocia/Control/GPIO-1_wiring_schematics

    #116062
    Profile photo of switchwire
    switchwire
    Participant

    Got it working! Thanks for the help.